 Post subject: Multi Generator two switchboard faults
PostPosted: Thu Nov 24, 2011 3:31 pm 
Offline

Joined: Sat Nov 20, 2010 10:17 am
Posts: 13
Location: Victoria British Columbia
I am currently working on a shipboard study. The ship has four 850 KW gen sets 450 Volt, two gen sets provide power to two switchboards which are coupled by bus ties.

Software limits the number of generators that can be connected at any given time to three.

The main gen sets are protected by ACBs which also have protection that will cause instantaneous trip at currents greater than 24 Ka.

Here is my problem, the arcing current with three generators is such that an instantaneous trip will occur, however if only one breaker trips, and this happens in or close to post the subtransient portion of the generators the current will then fall below the instantaneous level; so I could have a sustained arc as the remaining generators will now take up to .4 of a second to respond. In the instantaneous portion the Incident level is 8 Cals in the non instantaneous it rises to 27 cals.

My question do I need to consider this possibility or caculate the fault as though all breakers opened or the fault cleared.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sun Nov 27, 2011 5:19 pm 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1245
Location: Scottsdale, Arizona
This one is going to take some effort. It is more of a dynamic simulation and will require multiple calculations (although it sounds like you may have already performed them).

Should you include this type of simulation? I believe the simple answer is: If it can happen, it should be considred.

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883