When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ?
The above assumes that the current divides equally between the two 100A parallel fuses.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jan 24, 2012 5:12 am 
Offline
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1245
Location: Scottsdale, Arizona
mnewman wrote:
When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ?
The above assumes that the current divides equally between the two 100A parallel fuses.


What voltage? Medium Voltage fuses have a parallel mounting for larger ratings. i.e. 540E which is made up of 2 - 300E fuses in parallel. 540E = (2 x 300E) x 90% The curve is specific for a 540. I did not overlay a shifted 300E TCC with a 540E but it looks like the shapes are similar.

In the U.S. we don't parallel LV fuses (except perhaps cable limiters on networks)

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Jan 28, 2012 5:51 am 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1877
Location: North Carolina
There is a small problem with this. The average fuse rating doubles but the fuse accuracy goes down. Fuse curves show a range of values to accomodate a +/-% factor. If you parallel them, you might get a batch which are both on the extreme to either the positive (bad from an arc flash point of view) or negative side.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883