| Fuses in parallel https://brainfiller.com/arcflashforum/viewtopic.php?f=4&t=1989 |
Page 1 of 1 |
| Author: | mnewman [ Sun Jan 22, 2012 5:21 pm ] |
| Post subject: | Fuses in parallel |
When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ? The above assumes that the current divides equally between the two 100A parallel fuses. |
| Author: | Jim Phillips (brainfiller) [ Tue Jan 24, 2012 5:12 am ] |
| Post subject: | |
mnewman wrote: When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ?
The above assumes that the current divides equally between the two 100A parallel fuses. What voltage? Medium Voltage fuses have a parallel mounting for larger ratings. i.e. 540E which is made up of 2 - 300E fuses in parallel. 540E = (2 x 300E) x 90% The curve is specific for a 540. I did not overlay a shifted 300E TCC with a 540E but it looks like the shapes are similar. In the U.S. we don't parallel LV fuses (except perhaps cable limiters on networks) |
| Author: | PaulEngr [ Sat Jan 28, 2012 5:51 am ] |
| Post subject: | |
There is a small problem with this. The average fuse rating doubles but the fuse accuracy goes down. Fuse curves show a range of values to accomodate a +/-% factor. If you parallel them, you might get a batch which are both on the extreme to either the positive (bad from an arc flash point of view) or negative side. |
| Author: | alag13 [ Thu Dec 14, 2023 2:37 pm ] |
| Post subject: | Re: Fuses in parallel |
I know this was post was made a long time ago, but maybe someone can still respond. so Jim Phillips gave the example of two fuses in parallel. But I have a situation where I have a medium voltage switchgear with 3 fuses in parallel with a total amperage of 1080A between the three. What would be the calculation for that; what would each fuse size be? Thank you |
| Author: | bbaumer [ Thu Dec 14, 2023 3:50 pm ] |
Here's another thread on this subject, low voltage version. It was never resolved though. Like a lot of posts on here, people try to help and answer the question but the OP disappears with no follow-up. viewtopic.php?f=23&t=5609 You can model multiple fuses in parallel in SKM. Not sure about other programs. Never tried in etap and I don't have EasyPower. That said, RE: your question, what are you trying to calculate or are you only trying to select fuses? |
| Author: | alag13 [ Fri Dec 15, 2023 6:02 am ] |
I am trying to calculate the fuse size. I have never seen a triple barrel per phase before. They want 1080A between the three fuses per phase, but I cannot determine what the E-rated fuse would be. I want to know if there is a calculation behind determining this. |
| Author: | bbaumer [ Fri Dec 15, 2023 10:47 am ] |
To calculate fuse size you need to know what you are protecting. Are you trying to protect a transformer? A feeder? What size? What type of fuse or fuse holder? What type of switchgear will the fuses be installed in? I haven't seen a triple barrel fuse before either but it appears that you can buy them in CL-14. I only see up to 300E though. If you think you need 360E (x3=1080??) then it must not be a CL-14. Are you in the US or is this somewhere else? Is this existing switchgear or new? Do you have any cut sheets on the gear? Any other information? |