Author: | Superman Engineer [ Mon Feb 06, 2012 2:51 pm ] |
Post subject: | Transformer Voltage |
I have a single line diagram which mentions the transformer voltage as follows: 600/120/208V Could any one explain what does it mean? |
Author: | XLR8 [ Mon Feb 06, 2012 4:44 pm ] |
Post subject: | |
Most likely it is 600 volt delta on the primary and 208Y/120V on the secondary. 600V?? where are you / what type of system? |
Author: | Superman Engineer [ Fri Feb 10, 2012 2:28 pm ] |
Post subject: | |
Yeah I am there.. I got the answer from some other resource. Details are: 600V (Primary Delta phase to phase) / 208(secondary phase to phase) / 120 (secondary phase to neutral). |
Author: | glen1971 [ Mon Feb 13, 2012 5:56 am ] |
Post subject: | |
It's a fairly common voltage in commercial settings in Western Canada.. |
Author: | Vincent B. [ Mon Feb 13, 2012 9:43 am ] |
Post subject: | |
glen1971 wrote: It's a fairly common voltage in commercial settings in Western Canada.. I'd say it's really common across all of Canada. Up here, 480 V is for foreign equipment |
Author: | dhmcdonald [ Mon Feb 13, 2012 3:39 pm ] |
Post subject: | |
600V is the traditional transformer voltage rating on a system employing 575V motors, just as 480V is the standard transformer voltage on a 460V motor system. The difference in voltage ratings account for the voltage drop which almost always (except in the case of very short conductor lengths) exists from point of transformation to point of utilization. Very common in Canada and amongst process users (refiners, pulp producers, chemical plants and the like) in the US. As stated, rating implies 3 Ph Transformer 600V primary, 208Y/120V secondary. |
Author: | glen1971 [ Mon Feb 13, 2012 7:18 pm ] |
Post subject: | |
Vincent B. wrote: I'd say it's really common across all of Canada. Up here, 480 V is for foreign equipment Foreign equipment?? Don't know that I'd use that term... To find 600 volt in the oil and gas industry in Alberta (using it as an example as that is where I spend most of my time) would be rare... There are thousands of 480 volt installations province wide, both 3 phase and single phase.. |
Author: | Vincent B. [ Tue Feb 14, 2012 7:12 am ] |
Post subject: | |
glen1971 wrote: Foreign equipment?? Don't know that I'd use that term... To find 600 volt in the oil and gas industry in Alberta (using it as an example as that is where I spend most of my time) would be rare... There are thousands of 480 volt installations province wide, both 3 phase and single phase.. I agree there are some whole plants running on 480V in Canada, but it's not the standard across all sectors. In manufacturing plants (where I spend most of my time), 600V is standard, with the odd 480V transformer for one or two machines. Of course, even then there are some exceptions, where plants using a lot of foreign equipments add a 480V distribution across the whole plant. Here (Province of Quebec), the local utility only provides 600/347V or 240/120V for low voltage. If you want 480/277V, you must transform it yourself. |
Author: | Superman Engineer [ Wed Feb 15, 2012 11:27 am ] |
Post subject: | |
This single line was from a building in Alberta, Canada. |