 Post subject: NFPA70E-2012 PPE for Hazard Risk Categories (HRC)
PostPosted: Sun Aug 19, 2012 7:55 pm 
Offline

Joined: Sun Apr 24, 2011 5:00 pm
Posts: 12
Location: Stratham, West Australia
I have seen HRC 2A and 2B in PTW arc-flash software but can not find these categories and their corresponding Incident Energies in 2012 edition of NFPA70 Table 130.7(C)(16).
Can anyone comment on RHC 2A and 2B ?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 20, 2012 5:14 am 
Offline
Sparks Level

Joined: Tue Feb 24, 2009 7:05 am
Posts: 252
mwjnewman wrote:
I have seen HRC 2A and 2B in PTW arc-flash software but can not find these categories and their corresponding Incident Energies in 2012 edition of NFPA70 Table 130.7(C)(16).
Can anyone comment on RHC 2A and 2B ?

Never seen those either. Is it really a PTW thing or a site-specific choice?
Maybe HRC 2A asks for 8 cal/cm^2 of protection and HRC 2B asks for 12 cal/cm^2 of protection. It is at least plausible.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 20, 2012 9:17 am 
Offline
Sparks Level

Joined: Sun Sep 23, 2007 5:00 pm
Posts: 108
Location: Calgary, Alberta, Canada
Unfortunately ETAP, Easypower and SKM have WRONGLY included H/RCs in the software results table for incident energy results. It should not be there and should not show up on labels.

If you complete engineering incident energy analysis the electrician selects arc rated clothing based on the incident energy and working distance indicated on the label.

In your company's Electrical Safety Program define arc rated clothing by a "Level #." Level 0, Level 1 and Level 2 only. If you use the hazard/risk category tables then these levels would correlate to H/RC #s.

You cannot use the hazard/risk category information in 70E or CSA Z462 when you have engineering incident energy analysis completed.

Regards;
Terry Becker, P.Eng.
[url="http://www.esps.ca"]www.esps.ca[/url]


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Aug 20, 2012 10:45 am 
Offline
User avatar

Joined: Mon Aug 20, 2012 10:20 am
Posts: 6
Location: Elgin, Illinois
I assume you are talking about SKM PTW. Have you contacted SKM about this? They would be the ones to explain the meaning of HRC 2A or HRC 2B... I suspect it refers to a specific customer designation.
It is my experience that most of the software companies are very careful about using HRC designations on labels. Most of the labels I have seen, specifically say "PPE Category", or just "Category" so that workers can easily determine what PPE to use, if working on the equipment while energized.
HRC or Hazard Risk Categories only apply for a specific task. The HRC can vary from HRC 0 to HRC 4 for the same equipment, depending on the task being performed. According to NFPA 70E, If labels contain a Hazard Risk Category, it must be the highest Hazard Risk Category that applies for any task on the equipment being worked on.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Sep 03, 2012 6:58 pm 
Offline

Joined: Wed Jun 29, 2011 3:33 pm
Posts: 11
I'm guessing 2A refers to category 2 and 2B refers to category 2* in NFPA70E-2009. PTW still refers to the 2009 version of NFPA70E in the arc flash results summary tables etc. The 2 and 2* categories differentiation was removed during the 2012 update to NFPA70E.

And yes, SKM need to update their software.

If I have this wrong, feel free to set me right ...


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883