What assumptions are engineers making for utility arc flash studies for OH three-phase transformer bank secondaries?
(1) Do you automatically assume that the flash event will escallate into a three-phase event given the possible spacings for the physical XFMR installations?
It might be conservative to do so, and also able to be calculated with existing software.
(2) How do you treat unbalanced banks?
Assume three of the larger, so it could be calculated with existing software. It is assumed this is fuse protected, and the percentage impedance similar.
(3) Does the secondary connection (wye or delta) affect the results?
Software will ask for this and frankly I don't remember if there is a diffferent result.
(4) Do you count on "local" XFMR protection fuses to clear? What if the fuses are sized differently for each XFMR?
Software will typically determine what is the clearing device if modelled accurately. Typical software will not allow different fuse types so I would try the largest fuse and the largest transformer.
I have to tackle these calcs shortly as part of our study. I'm curious to know what others are doing.
We have worked with ETAP software which I am comfortable is as good as any and better than some. But there are still shortcomings: recently we needed to model plug in busway that is not within the library of conductors so we fudged a bit by using equivalent cables. It is good to be familiar with the disclaimers within NFPA70E that indicate even the most comprehensive study will not avoid all injury, but should reduce injury. Also it is good to be aware that most engineering studies start with an assumption and even though 20 steps later it might appear to be black and white calculations, much is determined by the initial assumption. It is good to verify what the consequences of the initial assumption are.