 Post subject: Query related to PPE
PostPosted: Tue Feb 25, 2014 8:08 pm 
Offline

Joined: Tue Feb 25, 2014 7:46 pm
Posts: 2
Hi,
Q1. Is there any necessity to consider PPE, hazard categories, arc flash boundries that already have type test certificate for internal containment?
Q2. As per Table 130.7(C)(10) in NFPA 70E 2012 regarding the PPE requirements, should the worker wear AR PPE (including Hood/shield/AR Coveralls) even the hazard category is CAT-1 or 2?

Request any one to please let me know about the answer for above queries at the earliest.. Thank u


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Feb 26, 2014 7:13 am 
Offline
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 711
Location: Rutland, VT
Q1: Not clear on what you are asking. Could you elaborate?

Q2: There is no Table 130.7(C)(10) in NFPA 70E-2012. Regardless see Table 130.7(C)(16) for PPE required by HRC.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Feb 26, 2014 3:52 pm 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1880
Location: North Carolina
When you say "internal containment" and you are referring to arc resistant switchgear, that certification only applies when the doors are closed and bolted shut. The qualified workers that have to open it up and work on it still need the information when the doors are open. If you are referring to AIC then no, false. A bolted fault is vastly different from an arcing fault.

With regards to Q2, that sounds like an older (pre-2012) 70E standard. Where are you getting this from? Even in the older standards, arc rated PPE was required up to H/RC 2, even going back to the 2004 edition. The big change in the 2009 edition is that "layering" such as wearing two sets of coveralls was eliminated from the tables as it had no scientific basis. The big change in 2012 was that "2*" disappeared, and H/RC 2 now requires EITHER a hood or a combination of a balaclava and a face shield. Both require safety glasses and several other items that you did not mention. You need to get an up to date Code book because there were a lot of changes in the new edtion and there will be even bigger changes in the 2015 edition.

If you can't afford to purchase an up to date copy, go to the [url='http://www.nfpa.org/']www.nfpa.org[/url] website. You can read ALL current NFPA standards for free. You just can't copy/paste or print from them and they are a little slow to change pages. Don't feel shy about this. I have frequently looked up some of the lesser known standards that I don't have the time or money to pay for just for one or two paragraphs of material.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 27, 2014 11:24 pm 
Offline

Joined: Tue Feb 25, 2014 7:46 pm
Posts: 2
Thank u very much Mr Paul for your reply.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883