It is currently Wed Oct 21, 2026 6:28 am
How are you performing incident energy calculations for metal clad switchgear above 15-kV?
Using the 1584 method 21%  21%  [ 4 ]
Using the Ralph Lee Method 42%  42%  [ 8 ]
Using the NFPA 70E Task Based Tables 11%  11%  [ 2 ]
Classifying equipment as "Extreme Danger" (above 40 cal/cm^2) 16%  16%  [ 3 ]
Other Method 11%  11%  [ 2 ]
Total votes : 19
 Post subject: Poll: Metal-enclosed Switchgear above 15-kV
PostPosted: Tue Mar 11, 2014 7:43 am
I would like to take a small poll or begin a discussion on potential approaches to provide adequate PPE recommendations to personnel exposed to an arc flash hazard on metal-enclosed switchgear above 15-kV.
PostPosted: Wed Mar 12, 2014 6:33 am
For industrial type facilities, I use EasyPower and it uses IEEE 1584 up to 15kV. Above 15kV, it uses Ralph Lee method.
For substations and utility overhead lines, I use ArcPro.
PostPosted: Wed Mar 12, 2014 8:41 am
Didn't answer the poll, as I currently only work up to 2300 kV, with the exception of two 46kV/2.3kV utility transformers, and I don't model the primaries on those transformers.
PostPosted: Sun Mar 16, 2014 12:33 pm
This poll has been moved to the Question of the Week.
Please see [url='http://arcflashforum.brainfiller.com/threads/incident-energy-calculations-for-switchgear-above-15-kv.3242/#post-15031'][the new link][/url]for it.
