Post subject: Poll: Metal-enclosed Switchgear above 15-kV Posted: Tue Mar 11, 2014 7:43 am |
|
Joined: Tue Mar 11, 2014 6:36 am Posts: 0
|
Hello, I would like to take a small poll or begin a discussion on potential approaches to provide adequate PPE recommendations to personnel exposed to an arc flash hazard on metal-enclosed switchgear above 15-kV.
|
|
Top |
|
 |
wbd
|
Post subject: Posted: Wed Mar 12, 2014 6:33 am |
|
Plasma Level |
 |
Joined: Wed May 07, 2008 5:00 pm Posts: 828 Location: Rutland, VT
|
For industrial type facilities, I use EasyPower and it uses IEEE 1584 up to 15kV. Above 15kV, it uses Ralph Lee method. For substations and utility overhead lines, I use ArcPro.
_________________ Barry Donovan, P.E. www.workplacesafetysolutions.com
|
|
Top |
|
 |
Voltrael
|
Post subject: Posted: Wed Mar 12, 2014 8:41 am |
|
Sparks Level |
 |
Joined: Tue Nov 12, 2013 6:31 am Posts: 238 Location: Port Huron, Michigan
|
Didn't answer the poll, as I currently only work up to 2300 kV, with the exception of two 46kV/2.3kV utility transformers, and I don't model the primaries on those transformers.
|
|
Top |
|
 |
Jim Phillips (brainfiller)
|
Post subject: Posted: Sun Mar 16, 2014 12:33 pm |
|
Plasma Level |
 |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1538 Location: Scottsdale, Arizona
|
This poll has been moved to the Question of the Week. Please see [url='http://arcflashforum.brainfiller.com/threads/incident-energy-calculations-for-switchgear-above-15-kv.3242/#post-15031'][the new link][/url]for it.
_________________ Jim Phillips, P.E. Brainfiller.com
|
|