Post subject: Maintenance Settings to Lower HRC and IE Posted: Thu Feb 12, 2009 11:13 am |
|
Sparks Level |
 |
Joined: Mon Nov 10, 2008 1:08 pm Posts: 60 Location: Cincinnat, OH
|
One thing that we have developed within our company are maintenance settings to lower hazards on equipment. Using PDC analysis we adjust settings, usually just instantaneous settings to the proper level to have an acceptable working level. Of course this throws coordination out of whack but we are using it solely when energized work is going to be done. Than the settings are set back after work is accomplished. My question is has any one else seen this or are practicing this? Is there any flaw in our reasoning that we are overlooking?
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Thu Feb 12, 2009 12:41 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
McFlash wrote: One thing that we have developed within our company are maintenance settings to lower hazards on equipment. Using PDC analysis we adjust settings, usually just instantaneous settings to the proper level to have an acceptable working level. Of course this throws coordination out of whack but we are using it solely when energized work is going to be done. Than the settings are set back after work is accomplished. My question is has any one else seen this or are practicing this? Is there any flaw in our reasoning that we are overlooking?
Very common concept, but typically done using a maintenence switch, like the Quick Trip system. That way it is comtrollable, we prefer the quick trip becasue it has a padlockable switch cover. We retrofit breakers with these systems all the time.
|
|
Top |
|
 |
wbd
|
Post subject: Posted: Thu Feb 12, 2009 3:02 pm |
|
Plasma Level |
 |
Joined: Wed May 07, 2008 5:00 pm Posts: 830 Location: Rutland, VT
|
Ditto to what Zog says. Without a specifically dedicated maintenance switch that will implement the maintenance trip settings, you have to have a strong policy/procedure/controls to insure that the settings are returned to the proper settings for coordination.
_________________ Barry Donovan, P.E. www.workplacesafetysolutions.com
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Thu Feb 12, 2009 3:53 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
wbd wrote: Ditto to what Zog says. Without a specifically dedicated maintenance switch that will implement the maintenance trip settings, you have to have a strong policy/procedure/controls to insure that the settings are returned to the proper settings for coordination.
I fthey dont get returned to the right settings, and it will eventually happen, and the plant trips off line because of it, well you know, let the blame game begin!
|
|
Top |
|
 |
McFlash
|
Post subject: Posted: Mon Feb 23, 2009 12:39 pm |
|
Sparks Level |
 |
Joined: Mon Nov 10, 2008 1:08 pm Posts: 60 Location: Cincinnat, OH
|
Any links to manufacturers of the quick trip system your are referring to??
Thanks for the comments too.
|
|
Top |
|
 |
Zog
|
Post subject: Posted: Mon Feb 23, 2009 1:24 pm |
|
Joined: Mon Jun 02, 2008 11:58 am Posts: 1103 Location: Charlotte, NC
|
McFlash wrote: Any links to manufacturers of the quick trip system your are referring to??
Thanks for the comments too.
http://www.utilityrelay.com
|
|