Arc Flash Forum
Maintenance Settings to Lower HRC and IE
https://brainfiller.com/arcflashforum/viewtopic.php?f=4&t=330
Page 1 of 1
Author:  McFlash [ Thu Feb 12, 2009 11:13 am ]
Post subject:  Maintenance Settings to Lower HRC and IE
One thing that we have developed within our company are maintenance settings to lower hazards on equipment. Using PDC analysis we adjust settings, usually just instantaneous settings to the proper level to have an acceptable working level. Of course this throws coordination out of whack but we are using it solely when energized work is going to be done. Than the settings are set back after work is accomplished. My question is has any one else seen this or are practicing this? Is there any flaw in our reasoning that we are overlooking?
Author:  Zog [ Thu Feb 12, 2009 12:41 pm ]
Very common concept, but typically done using a maintenence switch, like the Quick Trip system. That way it is comtrollable, we prefer the quick trip becasue it has a padlockable switch cover. We retrofit breakers with these systems all the time.
Author:  wbd [ Thu Feb 12, 2009 3:02 pm ]
Ditto to what Zog says. Without a specifically dedicated maintenance switch that will implement the maintenance trip settings, you have to have a strong policy/procedure/controls to insure that the settings are returned to the proper settings for coordination.
Author:  Zog [ Thu Feb 12, 2009 3:53 pm ]
I fthey dont get returned to the right settings, and it will eventually happen, and the plant trips off line because of it, well you know, let the blame game begin!
Author:  McFlash [ Mon Feb 23, 2009 12:39 pm ]
Any links to manufacturers of the quick trip system your are referring to??
Thanks for the comments too.
Author:  Zog [ Mon Feb 23, 2009 1:24 pm ]
http://www.utilityrelay.com
Author:  dpmac [ Mon Feb 23, 2009 4:03 pm ]
Depending on your breaker type, needs and your budget, in addition to many retrofit kit companies, many of the manufacturers offer some type 'Maintenance Trip" or "Arc Safe" kind of system.
http://www.phpbb.com/