 Post subject: IEEE 1584 ranges models
PostPosted: Sun Jul 13, 2014 8:57 pm 
Offline

Joined: Thu Jun 05, 2014 5:52 pm
Posts: 19
Section 5.1 of IEEE 1584 defines the voltage range as below:

[*]Voltages in the range of 208 V–15 000 V, three-phase.

Does it means phase to phase voltage or phase to ground voltage? I understand that single phase arc quickly evolves into three-phase arc per IEEE model but does it true single phase to ground mean phase to ground voltage? If that is a case, then 25kV system with single phase to ground less than 15kV would be appropriated to apply IEEE 1585 instead of Arcpro which conflicts with OSHA software recommendation.
=============================


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584 ranges models
PostPosted: Mon Jul 14, 2014 4:27 am 
Offline
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 711
Location: Rutland, VT
That is the 3 phase voltage which is phase to phase to follow convention.

7604 wrote:
but does it true single phase to ground mean phase to ground voltage?


Not sure what you are asking here. Please clarify.

7604 wrote:
then 25kV system with single phase to ground less than 15kV would be appropriated to apply IEEE 1585 instead of Arcpro which conflicts with OSHA software recommendation.


This is a moot issue since it is answered above as it is 3 phase voltage and would fall into the More than 15 kV column in OSHA Appendix E Table 3.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: IEEE 1584 ranges models
PostPosted: Mon Jul 14, 2014 6:03 pm 
Offline

Joined: Thu Jun 05, 2014 5:52 pm
Posts: 19
By definition, an electric arc is a visible plasma discharge between two electrodes that is caused by electrical current ionizing gasses in the air

wbd wrote:
That is the 3 phase voltage which is phase to phase to follow convention.


Varc < 15kV between two un-grounded conductors

wbd wrote:
This is a moot issue since it is answered above as it is 3 phase voltage and would fall into the More than 15 kV column in OSHA Appendix E Table 3.


25kV nominal voltage system with single phase to ground arcing ==> Varc < 15kV between un-grounded and grounded conductors

I understand the technical wording but my gut didn't feel the same.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883