Section 5.1 of IEEE 1584 defines the voltage range as below: [*]Voltages in the range of 208 V–15 000 V, three-phase. Does it means phase to phase voltage or phase to ground voltage? I understand that single phase arc quickly evolves into three-phase arc per IEEE model but does it true single phase to ground mean phase to ground voltage? If that is a case, then 25kV system with single phase to ground less than 15kV would be appropriated to apply IEEE 1585 instead of Arcpro which conflicts with OSHA software recommendation. ============================= |
|
| Author: | wbd [ Mon Jul 14, 2014 4:27 am ] |
| Post subject: | Re: IEEE 1584 ranges models |
That is the 3 phase voltage which is phase to phase to follow convention. 7604 wrote: but does it true single phase to ground mean phase to ground voltage? Not sure what you are asking here. Please clarify. 7604 wrote: then 25kV system with single phase to ground less than 15kV would be appropriated to apply IEEE 1585 instead of Arcpro which conflicts with OSHA software recommendation. This is a moot issue since it is answered above as it is 3 phase voltage and would fall into the More than 15 kV column in OSHA Appendix E Table 3. |
|
| Author: | 7604 [ Mon Jul 14, 2014 6:03 pm ] |
| Post subject: | Re: IEEE 1584 ranges models |
By definition, an electric arc is a visible plasma discharge between two electrodes that is caused by electrical current ionizing gasses in the air wbd wrote: That is the 3 phase voltage which is phase to phase to follow convention. Varc < 15kV between two un-grounded conductors wbd wrote: This is a moot issue since it is answered above as it is 3 phase voltage and would fall into the More than 15 kV column in OSHA Appendix E Table 3. 25kV nominal voltage system with single phase to ground arcing ==> Varc < 15kV between un-grounded and grounded conductors I understand the technical wording but my gut didn't feel the same. |
|