Time –Current Curves for Low Voltage ( =< 1000V a.c. ) Industrial Fuselinks
Fuse manufacturers such as GEC ( IPD ) type T fuselinks to BS88 publish time-current curves for the average pre-arc time ( melt time ) as a function of symmetrical rms current.

IEEE1584-2002 Section 4.6 Step 5 states :

For fuses, the manufacturer’s time-current curves may include both melting and clearing time. If so, use the
clearing time. If they show only the average melt time, add to that time 15%, up to 0.03 seconds, and 10%
above 0.03 seconds to determine total clearing time. If the arcing fault current is above the total clearing time
at the bottom of the curve (0.01 seconds), use 0.01 seconds for the time.

Question 1.
Is the fuse total clearing time ( pre-arcing plus arcing time ) :
- For t =< 0.03 sec Total clearing time = average pre-arcing time + 1.15 * average pre-arcing time.
- For t > 0.03 sec Total clearing time = average pre-arcing time + 1.10 * average pre-arcing time.

Question 2.
Would it be realistic to assume a minus 10% time tolerance for the pre-arcing time-current curve ?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883