 Post subject: DC systems; at what values does one stop worrying?
PostPosted: Sat Feb 21, 2015 7:16 am 
Offline

Joined: Mon Jul 23, 2012 10:36 am
Posts: 8
Are there values for DC systems that by imperical analysis or by experience have determined that below those thresholds, one does not need to worry about arc flash? In this forum and others, there seems to be a consensus that at 120 VAC, there is no need to worry about injury from arc flash. In NFPA 70E-2015 Table 130.7(C)(15)(B), it seems at less than <100 VDC one does not need PPE.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC systems; at what values does one stop worrying?
PostPosted: Sun Feb 22, 2015 12:37 pm 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1877
Location: North Carolina
Look through the Battcon archives which is the battery conference. Duke Power commissioned resrs by Kinetrics that show that at 130 VDC at 20 kA or less with fairly narrow spacing (1/4“), if you normalize the data to the maximum sustained arc at 0.8 seconds and 18“ working distance instead of the screwy 12“ and stretching the arc data to an impossible 2 seconds, it is right at 1.3 cal/cm2. Thiss covers typical 125 VDC substation battery arrays. The data also shows that Ammerman's theoretical model is off by a factor of 2-4 on the high side so for other cases, you can use that as an upper bound. Ammerman's model is also mentioned in 70E, Annex D.8. Also by using Hertha Ayrton's model or similar ones it becomes clear that around 20-30 VDC, an arc cannot exist irrespective of the current. To date we don't have good models of arc/air cooling so predicting whether an arc is self sustaining which is critical to predicting low voltage arc flash can't be done directly.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883