ekstra   ara
 Post subject: Arc Flash Study starting point
PostPosted: Mon Jun 01, 2015 6:46 am 
Offline

Joined: Thu May 02, 2013 4:19 am
Posts: 1
We are adding a new 480V panelboard to a facility that has already had an arc flash study performed. In order to label our new 480V panelboard, and assuming that the arc flash study is still accurate, can we use the first upstream transformer as a starting point for our calculations for our new panel?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study starting point
PostPosted: Mon Jun 01, 2015 9:20 am 
Offline
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 1880
Location: North Carolina
Yes and no.

Adding reactive loads changes the available fault current for the whole system. Most of the time this has a "barely moves the needle" effect. But not always. This may require changing existing labels upstream of the new loads.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study starting point
PostPosted: Mon Jun 08, 2015 7:26 am 
Offline
Sparks Level

Joined: Fri Apr 15, 2011 7:43 am
Posts: 164
Location: Colorado
I agree with Pauleng. The proper way is to have it studied or calculate the IE.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study starting point
PostPosted: Tue Jun 16, 2015 7:28 am 
Offline

Joined: Wed Jul 25, 2012 11:41 am
Posts: 1
Depending on the software and who did your study, it should be a simple matter to use the entire system model and add the new load information.

As PaulEngr mentions this new load information can affect equipment upstream, mostly on the shared secondary of the transformer.

Depending on the size of the transformer and load you are installing, the evaluation should take into account the transformer protection in case this needs to be modified to accept the new load, and prevent nuisance tripping.

_________________
Cheers,
Jeff MacKinnon

SparkyResource.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 3 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883