Do the tap settings on power transformers affect the ARCFLASH study enough for us to be concerned with them?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Apr 29, 2009 7:22 pm 
Arc Level

Joined: Thu Jan 10, 2008 8:49 pm
Posts: 520
Location: New England
Voltage is a variable in the ieee formula for calculating arcing current. So it would have some effect. You'd have to run the equation with the different tab positions to see how much. My gut feeling is that it won't have a big difference, but not sure.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Apr 30, 2009 12:48 pm 
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 428
Location: Spartanburg, South Carolina
The problem with accounting for taps is that there is no formula to determine impedance at different taps. Unless you have the test data on different taps, you can't accurately calculate the fault current.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue May 05, 2009 9:35 pm 
Sparks Level

Joined: Thu Oct 18, 2007 7:10 pm
Posts: 262
Location: NW USA
Large power transformers generally are sold with impedance at tap settings, but that information is probably long gone by the time an arc flash study is being conducted. One could theoretically include both extremes and study the effects at each location on downstream distribution system, but managing such a study will point out that perhaps the methods should include a little compromise for sake of practicality.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883