ekstra   ara
 Post subject: 120 Volt arc flash
PostPosted: Fri Nov 11, 2016 8:10 am 

Joined: Fri May 20, 2016 5:38 am
Posts: 5
I believe it to physically impossible to sustain an arc flash at 120 V but can someone point me to the proof? Can someone indicate where a code specifically states no arc flash PPE is required at 120 VAC?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 120 Volt arc flash
PostPosted: Fri Nov 11, 2016 9:17 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
williamrucki wrote:
I believe it to physically impossible to sustain an arc flash at 120 V but can someone point me to the proof? Can someone indicate where a code specifically states no arc flash PPE is required at 120 VAC?


https://drive.google.com/file/d/0B6mGRC ... lDSWM/view

I collected what exists all in one place. There's nothing per se saying it but no research I've seen so far says that it is possible.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 120 Volt arc flash
PostPosted: Fri Nov 11, 2016 9:23 am 

Joined: Fri May 20, 2016 5:38 am
Posts: 5
Thank you very kindle for the ultrafast response.

Bill


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 120 Volt arc flash
PostPosted: Mon Nov 28, 2016 8:52 am 

Joined: Mon Nov 28, 2016 8:44 am
Posts: 1
William - see if these two references help...

208-V Arc Flash Testing: Network Protectors and Meters. EPRI, Palo Alto, CA: 2010.
1022218

US Dept. of Labor, Interpretation Letter, 07/13/2015 – Selecting protective clothing based on
the IEEE National Electrical Safety Code, C-2, 2012


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: 120 Volt arc flash
PostPosted: Mon Nov 28, 2016 9:48 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
jdlaw1 wrote:
William - see if these two references help...

208-V Arc Flash Testing: Network Protectors and Meters. EPRI, Palo Alto, CA: 2010.
1022218

US Dept. of Labor, Interpretation Letter, 07/13/2015 – Selecting protective clothing based on
the IEEE National Electrical Safety Code, C-2, 2012


Eblen's testing (under EPRI) by the way is looking at what might be some rather extreme cases. High available fault currents with a type of meter socket that essentially looks like a rail gun tend to throw plasma out of them during a fault and give really high incident energy, and network protectors have the basic problem that it's really just about impossible to figure out what the "available fault current" is at any given time. There is at least one OSHA documented incident with each of these where a fatality occurred and so EPRI did equipment-specific testing on that type of equipment.

It is also very close to the threshold where incident energies start to climb. I used that one in my collection as well. I have not been able to nail down a specific threshold but somewhere in the neighborhood of 200-300 VAC is the point where almost irrespective of the available fault current and other initial conditions, incident energy won't get over 1.2 cal/cm2 to the point where even if the incident energy is less than predicted by the various equations, it is still high enough to be a concern.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883