Post subject: Equipment rating assumptions Posted: Thu Feb 09, 2017 7:47 am |
|
Joined: Mon Jul 26, 2010 10:55 am Posts: 65
|
All - If you were doing a survey on a building built in the late sixties, found no equipment labeling and could find no equipment information what equipment AIC rating would you assume? Most of the stuff we are talking about is FPE in the 100a - 400a range of disconnects, bus switches etc.... Thanks in advance...
|
|
Top |
|
 |
bbaumer
|
Post subject: Re: Equipment rating assumptions Posted: Thu Feb 09, 2017 9:13 am |
|
Sparks Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 227 Location: Indiana
|
Probably 10K from what you are describing and not knowing voltage or anything else. Real AIC is probably higher. Maybe much higher but can you say so for sure?
On very old unmarked branch breakers 5K. Worst case scenario. Same deal. Probably at least 10K but you don't know. 5K is the lowest rating I've ever heard of.
_________________ SKM jockey for hire
|
|
Top |
|
 |
PaulEngr
|
Post subject: Re: Equipment rating assumptions Posted: Thu Feb 09, 2017 12:34 pm |
|
Plasma Level |
 |
Joined: Tue Oct 26, 2010 9:08 am Posts: 2174 Location: North Carolina
|
5 kA is the correct rating for unmarked equipment. As mentioned the real rating is probably higher but that's what is the standard for unmarked ratings.
|
|