ekstra   ara
 Post subject: ARC Flash rating for electric meter removal
PostPosted: Wed May 13, 2009 12:56 pm 
Offline

Joined: Wed May 13, 2009 12:12 pm
Posts: 4
I am the safety director for a company that replaces and installs electric meters for utility companies across the US. I have been beating my head in the wall over this Hazard Risk Assessment. I have no clue where to start since it varies so much from one area or house to the other. I at this point require my men to wear PPE rated at 8 Cal for < 240 and 12.4 Cal for <480. I have read a few threads on here that state I should require atleast 20 Cal for my 3 phase installers. Can anyone shed some light on this turmoil I have here? :confused:


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri May 15, 2009 6:03 am 
Offline

Joined: Wed May 13, 2009 12:12 pm
Posts: 4
I suppose no one has had a situation like this before. I have seen alot of talk about single and three phase meters on these forums. I am just having a hard time with analyzing the hazard risk factor and I thought maybe someone could give me a worst case scenario for ARC flash rating on a a single phase and three phase


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri May 15, 2009 7:45 am 
Offline

Joined: Thu Jan 29, 2009 2:06 am
Posts: 29
You are not going to be able to do single phase. You can treat the mete socket as a bus in order to determine the fault currents in your modeling, I suppose.

I do know they make these:
http://www.rauckmanutility.com/homemeterpuller.htm


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon May 25, 2009 6:22 pm 
Offline
Arc Level

Joined: Wed Jun 04, 2008 9:17 am
Posts: 411
Location: Spartanburg, South Carolina
If the work is on utility meters, then it is covered by NESC. The NESC has a general 4 cal/cm² for systems below 1000V if an incident energy (IE) analysis is not made, and a clothing system to match the IE if it is calculated. It doesn't specify what method to use if an analysis is done.

The problem is, if you use IEEE-1584 for low voltage metering fed by large transformers with no secondary protection, you will calculate IE much greater than 4 cal/cm² and greater than 40 cal/cm² in many cases. It is generally recognized that 4 cal/cm² is not adequate in many cases. There are proposals to add a table to the next NESC that would use 20 cal/cm² for 480 volt systems.

See the NESC section of this forum for more discussion.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 28, 2009 5:52 am 
Offline

Joined: Wed May 13, 2009 12:12 pm
Posts: 4
Yea I have seen the meter puller before but they are costly. I had heard from some utility companies that a small ARC Flash could come from a meter base carrying 240 volts or less. I already make my guys wear gear rated at 8ATPV just in case. I appreciate the info. If you know of anywhere I can see testing of a 240volt meter base please let me know


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 28, 2009 5:56 am 
Offline

Joined: Wed May 13, 2009 12:12 pm
Posts: 4
Yea I have made my guys working on 240volts or less wear PPE rated at 8 cal/cm just in case. I plan to move my employees working with 480 volts into the 20 cal/cm as soon as possible. Thanks for the info. Jghrist


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883