 Post subject: Query on IA (internal arc) classified board
PostPosted: Wed Aug 09, 2017 6:22 pm 
Offline

Joined: Wed Aug 09, 2017 6:58 am
Posts: 2
Hi Guys,

I am new to the forum and the topic of arc flash as well. The query I have is if a board is IAC rated for 25kA, 1sec, would the board be treated as being able to perform its (arc withstand) function adequately in the following circumstances?

a. Arc fault with lower current but higher duration than what the board is classified for - for example 15kA, 2 sec
b. Arc fault with higher current but lower duration than what the board is classified for - for example 30kA, 0.5sec

If the answer to any of the above questions is a yes, I would be keen to understand how the situation is assessed and if there is/are any reference paper/s discussing the topic? From my limited knowledge, I think it is not a matter of simply comparing the incident energy (i.e. if the incident energy calculated for an arc fault is lower than the incident energy calculated from the board IAC rating then all is good). I would be keen to have your thoughts on this. Thanks in advance.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883