| Author: | stevenal [ Thu Mar 15, 2018 8:27 am ] |
| Post subject: | Re: Question about table 410-2 ieee.c2. vs arcpro |
The table uses line to line voltage, but when finding arc length the note 1 says to divide the line to ground kV by 10. Your calculated arc gap should be divided by sqrt(3). When I've looked at this in the past, I found the tables did not necessarily correspond to the MADs in the same revision of the NESC. Looking back a revision or two produced better results. Why 9.3 cycles? Tabulated value is 11.9. Might try changing the electrodes; I forget which gave better results. |
|