 Post subject: Incident Energy - 30A Disconnect
PostPosted: Wed Nov 21, 2018 12:05 pm 

Joined: Wed Nov 21, 2018 12:00 pm
Posts: 1
Has anyone come across incident energy over 8 cal for a 30A 480V disconnect?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Thu Nov 22, 2018 7:53 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1492
Location: Scottsdale, Arizona
Swizzle wrote:
Has anyone come across incident energy over 8 cal for a 30A 480V disconnect?


It can happen.

Since the arc duration is usually defined by how long it takes an upstream overcurrent device to clear the arcing current, a larger incident energy is often due to a longer clearing time from that device.

What device is upstream? Do you have a clearing time from the study result?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Fri Nov 23, 2018 10:12 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
Easier than that if it's fed by one big transformer like say a 1000 kva.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Mon Nov 26, 2018 8:50 am 
User avatar

Joined: Mon Jan 24, 2011 11:25 am
Posts: 35
Location: richmond, VA
we have it happen quite often in our Quarries. When you go 1500 feet of cable to a pump down in the pit the short circuit current goes low and the trip time on the Circuit breaker becomes long.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Tue Nov 27, 2018 12:57 pm 
User avatar

Joined: Wed Jul 03, 2013 12:28 pm
Posts: 2
Typically happens at test switches or switches for power factor correction (or PQ monitoring) that are tapped off the main bus of 480 V switchgear. Why those switches are installed the way they are is another topic. ;) As many have pointed out, it's what's upstream that matters.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Wed Dec 05, 2018 8:50 pm 
Sparks Level

Joined: Sat Nov 21, 2009 10:23 pm
Posts: 107
Location: Ohio
The question would be more interesting if we discussed the possibility of exceeding 1.2 cal down stream from a 30A or 60A fuse and or breaker. For those that use arc flash software try and get the incident energy above 1.2 cal down stream from a Mersen A6K200R or Buss KTSR200.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Incident Energy - 30A Disconnect
PostPosted: Mon Dec 10, 2018 6:58 pm 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
Flash wrote:
The question would be more interesting if we discussed the possibility of exceeding 1.2 cal down stream from a 30A or 60A fuse and or breaker. For those that use arc flash software try and get the incident energy above 1.2 cal down stream from a Mersen A6K200R or Buss KTSR200.


That seems to be the case regardless of the make or model of device once you get down below about 150%.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883