PostPosted: Fri Nov 30, 2018 5:45 am 

Joined: Wed Jul 12, 2017 6:06 am
Posts: 27
When collecting data in facilities using bus ducts, are you guys tracing every bus plug and modeling or just getting the data for the larger bus plugs? We recently quoted a facility with very tall ceilings and all the conduit is painted ceiling color. It will be very time consuming to trace every bus plug circuit. Three of the ducts are about 400 feet long and loaded with equipment and none of them are labeled as to what they feed.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Fri Nov 30, 2018 11:13 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 821
Location: Rutland, VT
Are the bus plugs labeled? Then you should know what equipment it feeds. They should be labeled.
Are you going up and opening each bus plug to get the fuse data? If so and the plug is not labeled with the equipment it feeds, you can clip on a tracer and someone on floor can find it.
If not going to open plugs to get fusing, then are you opening the end equipment and basing fuse size on wire size?

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Sat Dec 01, 2018 12:57 pm 

Joined: Wed Jul 12, 2017 6:06 am
Posts: 27
wbd wrote:
Are the bus plugs labeled? Then you should know what equipment it feeds. They should be labeled.
Are you going up and opening each bus plug to get the fuse data? If so and the plug is not labeled with the equipment it feeds, you can clip on a tracer and someone on floor can find it.
If not going to open plugs to get fusing, then are you opening the end equipment and basing fuse size on wire size?


Nothing is labeled in this place. That’s my main reason for the question. Some of the conduit runs are over 100’ away from the duct. Is acceptable to size fuses from wire in equipment?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Sun Dec 02, 2018 7:21 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 821
Location: Rutland, VT
That depends. Does the facility adhere to the NEC when installing the circuits? If you feel comfortable that they do, then you can state that in the report and do that as an assumption.
Although if nothing is labeled, that is an issue. How do they do lockout tagout if they don't know what bus plug goes where?

Are the bus plugs going to be labeled? If so, you going to be up at it, so might as well open it and get the fuse size.

I think the best thing is to put a circuit tracer on each circuit and determine where it is fed from. Circuits need to be labeled and not being so is probably a NEC and OSHA violation and I am not where I can look that up.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Sun Dec 02, 2018 10:36 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
There are a variety of reasons wire size exceeds required ampacity...convenience, lack of knowledge, multiple feeders in a common raceways, voltage drop, etc. If you oversize the fuse assumption based on wire size, your incident energies will be much higher.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Sun Dec 02, 2018 1:25 pm 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 821
Location: Rutland, VT
PaulEngr wrote:
There are a variety of reasons wire size exceeds required ampacity...convenience, lack of knowledge, multiple feeders in a common raceways, voltage drop, etc. If you oversize the fuse assumption based on wire size, your incident energies will be much higher.


True but since they are off of a bus duct typically fault currents have dropped and the fusing is usually 100A or less, so higher IE's may not be a big issue. For example, 4 cal/cm2 with fuse actually known and 6 cal/cm2 with fuse size estimated.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Mon Dec 03, 2018 7:19 am 

Joined: Wed Jul 12, 2017 6:06 am
Posts: 27
wbd wrote:
That depends. Does the facility adhere to the NEC when installing the circuits? If you feel comfortable that they do, then you can state that in the report and do that as an assumption.
Although if nothing is labeled, that is an issue. How do they do lockout tagout if they don't know what bus plug goes where?

Are the bus plugs going to be labeled? If so, you going to be up at it, so might as well open it and get the fuse size.

I think the best thing is to put a circuit tracer on each circuit and determine where it is fed from. Circuits need to be labeled and not being so is probably a NEC and OSHA violation and I am not where I can look that up.


Each machine has a local disconnect at it, that is how they lock out. I agree circuits should be labeled, but often in the real world they are not. I have been in several industrial facilities and this is probably one of the worst I have seen. The main switchboard has an 800-amp and two 500-amp circuits and they arent even labeled as to what they feed. Luckily these conduits are easy to trace. A bus duct with 150 different 3/4" and 1/2" conduits coming off and going in different directions in a 40' ceiling, not as simple. Sounds like the best thing going forward is to make sure we allow a ton of data collection time in facilities like this.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Mon Dec 03, 2018 10:18 am 

Joined: Fri Nov 06, 2015 1:05 am
Posts: 25
Location: Evansville IN
The simple answer is YES we do trace all bus plugs
We have 7 miles of bus way, 2700 bus plugs.
We also have an additional 7000 pcs of equipment which 6000
of these are studied.
Yes it was a large task and is nearly complete. We are approaching the two year mark.
The key is planning and managing the team. We also had a large contractor (electrical) that was
familiar with out facility use Arial lifts for most of the bus way work.
We have one of the largest models Easy Power has seen.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Mon Dec 03, 2018 1:16 pm 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 187
Location: Maple Valley, WA.
We too get the bus plug data and also create an AF label the them. Making too many assumptions when performing an arc flash study can land yourself in court. Accurate data collection at existing facilities is important and can be 50 -60% of the total cost of performing an arc flash study.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Fri Dec 14, 2018 2:12 pm 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 134
We always get the bus duct disconnect or breaker data and we do create labels to go on the device as well as on the machine that's being fed. We also get the length of the bus, the brand, amperage and all the rest. The hazards are often much higher at the bus duct disconnect than at the machine disconnect. If no one ever goes near the bus, no worries, but what if they do?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Bus Duct Data Collection Question
PostPosted: Sat Dec 15, 2018 7:19 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2174
Location: North Carolina
wilhendrix wrote:
We always get the bus duct disconnect or breaker data and we do create labels to go on the device as well as on the machine that's being fed. We also get the length of the bus, the brand, amperage and all the rest. The hazards are often much higher at the bus duct disconnect than at the machine disconnect. If no one ever goes near the bus, no worries, but what if they do?


Anyone with an experience operating old breakers and disconnects that are never operated can tell you that they seize up under the spring tension as the grease is pushed out of the bearing surface by mechanical force. After even 3-5 years it gets to be a crap shoot with breakers. With disconnects after about 10 years often they never open again.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 11 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883