bbaumer wrote:
1. Check to see if you already have a series combination. What are your upstream and downstream breakers?
2. Check to see if you can add current limiting fuses upstream to get a series rating.
3. Replace the breakers with 42K breakers.
4. Double check the actual installed feeder length.
Unfortunately the circuit breakers that were used do not have a series rating provided by the manufacturer. The main distribution panel (which feeds all others on the mezzanine) has mostly breakers rated at 42k. We are in the process of swapping out the couple rated for 35ka to those which are rated for 42kA. This resolves the issue with the main panel. Just received confirmation on all feeder lengths.
Replacing breakers in the downstream panels is an option but I need to exhaust all other options first. These are brand new panels built over seas that make use of several breakers in each cabinet.