 Post subject: Lee method
PostPosted: Thu Apr 18, 2019 1:40 pm 

Joined: Thu Apr 18, 2019 1:33 pm
Posts: 2
What is the general opinion about the lee method?
From my perspective, calculating the incident energy for 33 kV systems, is a shot way above the goal or is it?
/ Thanks in advance, Thomas


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Lee method
PostPosted: Fri Apr 19, 2019 3:52 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 825
Location: Rutland, VT
You should be using ArcPro to determine the incident energy for 33kV systems. Not sure where you are located but this is the method recommended by OSHA here in the USA.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Lee method
PostPosted: Fri Apr 19, 2019 6:10 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1509
Location: Scottsdale, Arizona
thonie96 wrote:
What is the general opinion about the lee method?


It was a good beginning back in the early 1980's but being theoretical, voltage was a heavily weighted component in the calculation. The higher the voltage, i.e. 33kV, the more "conservative" (shooting higher above the goal) it became. It trends orders of magnitude higher at higher voltages.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883