It is currently Sun Oct 25, 2026 5:32 pm
 Post subject: Pre-fault Voltage
PostPosted: Thu Sep 26, 2019 10:22 am
When conducting fault current calculations prior to deriving incident energy values, does anyone run multiple scenarios with different pre-fault per unit voltage values?
Thanks for the input.
 Post subject: Re: Pre-fault Voltage
PostPosted: Sat Sep 28, 2019 4:00 am
Back in my electric utility days we would run V at 1.05 p.u. as a what if in the event transformer taps boost the voltage by 5% I don't if too many others take this approach. It really becomes important when the fault current is close to the interrupting or withstand rating.
PostPosted: Mon Sep 30, 2019 7:49 am
I normally run three scenarios; Base analysis, utility drop by 10%, and all motors off. The 10% voltage drop (0.9 utility voltage) is to take care of a heavily loaded utility system.
PostPosted: Mon Sep 30, 2019 10:46 am
We typically do not change the prefault voltage. Instead we run multiple scenarios. (1) Infinite Utility fault current (when primary fault current is not known) with motors on; (2) Double the Utility transformer Impedance with motors off. If the system has emergency generators, then we run additional scenarios with (3) Generator On - Motors on and (4) Generator On with motors off.
This will produce the maximum and minimum fault currents for each location.
