The Table should have been constructed as a means to model typical US business industrial electrics.

"Panelboards or Switchboards Rated >240 and up 600V with molded case or insulated case circuit breakers - Note 1"

Note 1: Maximum or 25kA short circuit available, maximum 2 cycle fault clearing time.

Wouldn't you say that 25kA is atypically low? How many 480 switchboards are there in US businesses that are fed directly from the utility transformer which are often 1000KVA, 1500KVA, and even 2000KVA? Why would they pick such a low value?

Lets say we have something more typically industrial in the 35kA to 45kA range - what then. I take it we can't just use the 'switchgear' section whose footnote is max 65kA because it says 'power circuit breakers'.

What is the economical solution to deal with switchboards at industrial fault levels. I'm talking the classic Square D switchboard, main breaker compartment with attached I-Line distribution panel.

Further, lets say the fault is unders 25kA and there is a main circuit breaker. I think its safe to say that the utility is not using a primary fuse that will clear in 2 cycles for a secondary arc fault. So then we can't use the Table for the main. But if the main does clear under 2 cycles, can we use the Table on the distribution side of the cabinet? Is this prohibited because the fault on the load side of the main could carry over to the line side?


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 1 post ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883