 Post subject: MV over 15Kv Load/Non Load Break Elbows
PostPosted: Thu Apr 30, 2020 8:06 am 
User avatar

Joined: Mon Nov 05, 2007 10:10 am
Posts: 48
Location: Mid-West
been searching around the forum and some other resources, and would like to get other opinions on dealing with pad mounted transformers and pad mounted medium voltage switchgear operating above the 15kV lelev that uses IEEE separable connector load break elbows, dead front equipment with the equipment doors open these would be removed phase at a time with a hot stick type approach, it appears that the line to ground fault exposure would be the worst case then reading and researching hearing about the ability for the elbow connector to deform or possibly “explode” in colder climates although appears the manufacturers have addressed the issue. Curious on thoughts of everyone in the forum. Thanks..


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: MV over 15Kv Load/Non Load Break Elbows
PostPosted: Mon May 04, 2020 8:12 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 188
Location: Maple Valley, WA.
I agree that the worst case fault would be a line to ground fault. The chances of a line to ground fault to propagate to a 3 phase line to ground fault is extremely low for dead front equipment. However, OSHA states that you must use 3 phase bolted faults to determine the AF energy level in enclosed equipment.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: MV over 15Kv Load/Non Load Break Elbows
PostPosted: Wed May 06, 2020 8:49 am 
Sparks Level

Joined: Sat Nov 21, 2009 10:23 pm
Posts: 110
Location: Ohio
If you are interested in MV padmount transformers, you should take a look at the NESC and the testing/white papers that led up to the NESC results.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2019 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883