| Author: | Jim Phillips (brainfiller) [ Mon Jan 25, 2021 6:43 am ] |
| Post subject: | Re: Insulating barriers installed between electrodes |
As you found, there is still limited information for every arc flash situation. IEEE 1584 assumes there are no barriers between the bus. Many would assume "worst case" with no barrier with the reasoning, what if it was removed, damaged, melted - basically some justification for calculating a straight line between the buses. Could that happen? Who knows but when legal minds get involved.... Others may have different views, but this is a pretty common one. How does it affect the incident energy? Remember in the end it is all about making sure the worker is protected from the arc flash should there be energized work (which it to be avoided unless justified based on NFPA 70E) Do the different assumptions result in higher arc ratings for PPE? |
|