If an arc flash is performed, how many years it's valid for. I heard 5 years is mentioned in NFPA 70E?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash validity
PostPosted: Mon Dec 06, 2021 6:55 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
It is from NFPA 70E 130.5(G) Incident Energy Analysis Method.

The incident energy analysis shall be updated when changes occur in the electrical distribution system that could affect the results of the analysis. The incident energy analysis shall also be reviewed for accuracy at intervals not to exceed 5 years.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash validity
PostPosted: Mon Dec 06, 2021 9:49 am 
Sparks Level
User avatar

Joined: Tue Oct 26, 2010 5:00 pm
Posts: 201
Location: Maple Valley, WA.
Note that NFPA 70E states that the study must be "Reviewed" and does not mention anything about being "Valid". In other words, the study may not be needed to be re-performed if there have not been any major changes to the distribution system or electrical equipment.

However, the IEEE 1584 Standard has been revised and now requires additional data to calculate the arc flash energy. If your study was performed before September 27th, 2018, then it will need to be re-performed using the new IEEE-2018 Standard.

_________________
Robert Fuhr, P.E.; P.Eng.
PowerStudies


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883