A few thoughts - others may add to this. Also, this is not any formal interpretation or engineering opinion, just a few things to consider (legal disclaimer)
SamoKablamo wrote:
Hello everyone, here are some questions I have about arc flash policies. I am thinking mainly in terms of 70E and 1584, and I'm in the industrial world (mining, power generation, etc).
1. Many sites have a rule that says "no live work". If indeed that rule is followed 100%, what need is there for an arc flash study? (Besides letter of the law.)
The process of creating an electrically safe work condition per NFPA 70E requires absence of voltage testing which is considered live work. I have a few cases where a system was believed to be de-energized but wasn't. One resulted in a huge arc flash and debilitating injury when they "thought" it was de-energized.
SamoKablamo wrote:
2. I often see that the arc flash safety rules are applied as if the doors were open, even when they are not. So the AF boundary, PPE requirements, etc are applied whenever the equipment is live regardless of the presence of exposed conductors. What do you say about this policy? The inconsistency there is this: if we are acting like switchgear, MCCs, panelboards, etc are dangerous with the doors closed, why do we not put labels on motor terminal boxes, cable tray, etc? (I'm not arguing that they are not dangerous with the doors closed, just pointing out the inconsistency.)
Two things here. Doors open statement applies when an arc flash hazard exists. Examples: Energized work being conducted, interaction that could result in an arc flash etc. IEEE 1584 calculations are based on doors open because unless the equipment uses an arc resistant design, there is no way to know if the doors will remain closed during an arc flash - blast pressure.
The second part is if there isn't an arc flash hazard - no interaction, then the arc flash boundary doesn't exist. i.e. simply walking down a corridor with equipment nearby doesn't trigger an arc flash boundary.
SamoKablamo wrote:
3. I've been to sites where you have to wear the PPE, including maybe a bomb suit, any time you enter the AF boundary when the equipment is live. I've been to sites where you don't need any special gear in the AF boundary unless you are operating a breaker, and then you wear FR clothes and a face mask if you are operating a breaker. And I've been to other sites that require no extra PPE unless a door is open to live conductors. I think all of these are in compliance to 70E, but it's crazy how differently they interpret it. Thoughts?
Some of this depends on the severity of a prospective arc flash. PPE is required for any part of the body within the arc flash boundary. That is the area where the incident energy exceeds 1.2 cal/cm^2 which is the threshold for arc rated PPE. It also depends on the likelihood of occurrence of an arc flash - NFPA 70E provides a table for this. Equipment condition, condition of maintenance play a role in this decision.
SamoKablamo wrote:
4. Is there a way to determine the hazard of an arc flash that happens when a door is closed? With the variety of equipment and manufacturer terms like arc resistant, arc proof, ducted, top venting, etc, how can we determine the hazard for someone standing in front of elec equipment when the door is closed and latched? I imagine we could have a statement by the manufacturer that says something like "when the door is shut and secured, the IE levels are reduced by 80%" for example. Instead of applying the hazard conditions of an open door scenario to a closed door scenario.
Arc resistant equipment is designed to offer protection to the worker when the equipment is properly used, doors closed etc. I saw 15 kV arc rated switchgear being test several years ago. I was in another area of the test facility conducting my own testing and didn't know they were about to test. When it happened it sounded like the end of the world but.... It was a successful test.
SamoKablamo wrote:
5. Another nuance to this is when you have a door open to a control voltage compartment that is "isolated" from the higher voltage, but not as protected as if the door was closed and you were just standing in front of the gear. I'm thinking specifically of Eaton medium voltage MCCs. The lower door opens to the MV breaker, and the upper door opens to the control wiring and the back of the motor protection relay. It's often necessary (especially during commissioning) to be working the control voltage compartment while the MV below is energized. Another similar situation is when you get a 480V MCC with an integrated PLC or networking cabinet. There is usually the main horizontal bus behind the control cabinet back wall. Should the electrician be dressed in full PPE according to the AF label whenever they are in the controls?
This would be part of a risk assessment. What is the likelihood of an arc flash occurring if no one is directly interacting with the power side of things.
SamoKablamo wrote:
6. Do you put labels on every MCC starter bucket, one on each vertical section, or one for the entire lineup (or 2 if you have different IE levels for the MCB vs feeders and starters)?
There isn't a standard for this but most will place at least one label and maybe two depending on the physical size of the equipment and whether they are using the main device to define the arc duration for the feeders. There is nothing to prohibit a label on each cubicle but the front of the equipment will be very crowded with labels.
SamoKablamo wrote:
7. Do you calculate and make labels for PLC cabinets, network racks, etc with 120V? (Every site I've gone to has excluded these from the study-- seems inconsistent to me.)
Technically NFPA 70E applies to 50V and greater but what you cite is common.
SamoKablamo wrote:
8. Is there an official interpretation of IEEE 1584's comment about applying the line side IE levels of a main breaker to the entire lineup if it is not adequately isolated-- aka escalating faults?
This requires care and judgement. For switchgear, many have one calculation for the main based on the clearing time of an upstream device - often a utility device that may be quite slow. The the arc duration of the feeders are based on the main.