Hi all,

I received a task to convert a ETAP project file to SKM. I am wondering I should use the operating contribution or SC value.
My thinking is I should use the SC value, am I right?


Attachments:
ETAP Utility.pdf [48.38 KiB]
Downloaded 111 times
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP to SKM, Which Utility Contribution for Analysis
PostPosted: Fri Jan 19, 2024 10:27 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 383
Location: Indiana
Not sure how to answer your question but if your etap model is large I would send it to SKM and let them convert it for you if they can. I have faced this situation twice. The first time was a decent size model, 800+ busses. They were able to convert it no problem. When you get it back it won't have any drawings but the model will be in there. You have to start a new drawing with an existing component and expanded it all out and clean it up as you go.

The second time was a very small model. Maybe like 30 busses or something. SKM couldn't convert it for some reason. I spent more time sending them various etap files trying to help them to convert than it would have taken me just to re-draw it in SKM to begin with. They never were able to convert it. Never figured out why.

That first model conversion though saved me several days of work vs. recreating the model in SKM plus it probably eliminated some data entry errors.

https://www.skm.com/convert.html

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: ETAP to SKM, Which Utility Contribution for Analysis
PostPosted: Mon Feb 12, 2024 9:21 am 

Joined: Mon Nov 25, 2013 8:03 am
Posts: 8
Ground MVA in SKM is VLN*I, in ETap is is VLL*I*3^.5, but ETap displays both methods of entering ground. The trick is to show the ground amps, amps is amps, make sure that both programs show the same amp value.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883