While doing arc flash calculation, should we consider the Peak kA or RMS value.

Wouldn't it be a conservative way to consider the Peak short circuit ? or is it plain wrong

thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Short circuit Peak or Short Circuit RMS while doing ArcF
PostPosted: Thu Sep 26, 2024 5:37 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
It is the bolted rms symmetrical fault current. Plus evaluating different scenarios, max and min etc. to see if it affects overcurrent device operation. If you are about to undertake an arc flash study, you might want to take a deep dive into the standard and all of it's moving parts. There is a lot to know.

The "Training" menu item above takes you to IEEE 1584 / Arc Flash training and there are a few free classes, articles and videos on the subject to help.

Check back if you have more questions.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883