| Author |
Message |
Adithian
Post subject: Short circuit Peak or Short Circuit RMS while doing ArcFlash Posted: Wed Sep 25, 2024 2:55 am |
While doing arc flash calculation, should we consider the Peak kA or RMS value.
Wouldn't it be a conservative way to consider the Peak short circuit ? or is it plain wrong
thanks
| Top |
mpparent
Post subject: Re: Short circuit Peak or Short Circuit RMS while doing ArcF Posted: Thu Sep 26, 2024 11:47 am |
Have you read the IEEE 1584 standard?
| Top |
Jim Phillips (brainfiller)
Post subject: Re: Short circuit Peak or Short Circuit RMS while doing ArcF Posted: Thu Sep 26, 2024 5:37 pm |
| Plasma Level |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1736 Location: Scottsdale, Arizona
It is the bolted rms symmetrical fault current. Plus evaluating different scenarios, max and min etc. to see if it affects overcurrent device operation. If you are about to undertake an arc flash study, you might want to take a deep dive into the standard and all of it's moving parts. There is a lot to know.
The "Training" menu item above takes you to IEEE 1584 / Arc Flash training and there are a few free classes, articles and videos on the subject to help.
Check back if you have more questions.
| Top |
Page 1 of 1
[ 3 posts ] |
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot post attachments in this forum