Do you guys coordinate your ground fault trip settings? And do you ever coordinate those with the Phase settings?

Author:  mpparent [ Tue Oct 01, 2024 10:25 am ]
Post subject:  Re: Coordinating Ground Fault Trip

Yes and yes. In terms of coordination w/ "phase settings": I will take my upstream GF curve and coordinate it (as much as practicable), with a downstream molded case CB...say 20 or 30A.

Mike