Do you guys coordinate your ground fault trip settings? And do you ever coordinate those with the Phase settings? |
| Author: | mpparent [ Tue Oct 01, 2024 10:25 am ] |
| Post subject: | Re: Coordinating Ground Fault Trip |
Yes and yes. In terms of coordination w/ "phase settings": I will take my upstream GF curve and coordinate it (as much as practicable), with a downstream molded case CB...say 20 or 30A. Mike |