| Author |
Message |
jsoar
Post subject: Arc Flash Results Posted: Mon Mar 10, 2025 7:23 am |
Hello, I am working on this Arc Flash study for a company that wants the Incident energy levels below 4 cal. I can figure out why these ones are so high.
| Attachments: |
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 7:56 am |
| Arc Level |
_________________ 90% Retired
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 8:00 am |
| Arc Level |
Also, is that EasyPower? Should your most downstream feeders be 3-1/C, not 1-1/C? Not an EasyPower user so not sure. Attachment:
| Top |
jsoar
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 10:46 am |
Hey, I posted the Arc Fault from the bus. And yes this is easypower. Do i have the conductors wrong? 3-1/C instead of 1-1/C?
| Attachments: |
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 11:11 am |
| Arc Level |
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 11:28 am |
| Arc Level |
I looked at the curves with the XT4-N set to MIN. It looks like your energy is based on the A2A breaker tripping. At 1900 amps you are in the tolerance band of the breaker and it doesn't trip until well past 2 seconds. That is why you are timing out. You could re-run your study to look at both the line and load side of the main and use the line side with the upstream XT4-N breaker tripping in the instantaneous region. That will get your energy down, I think, on the one that is 1900A arcing current set to MIN. The ones that are only 1200A, neither breaker trips quickly and you still have your "high" incident energy. Attachment:
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 11:37 am |
| Arc Level |
| Top |
jsoar
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 11:49 am |
Lower Voltages: For voltages lower than 208V, some engineers use a shorter tripping time, such as 0.5 seconds, as the arc flash hazard is generally considered lower.
I found this on google.
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Mon Mar 10, 2025 12:01 pm |
| Arc Level |
| Top |
JBD
Post subject: Re: Arc Flash Results Posted: Thu Mar 13, 2025 9:23 am |
Joined: Mon Jan 18, 2010 11:35 am Posts: 614 Location: Wisconsin
jsoar wrote: I found this on google. I have not found AI to be very good at technical/engineering topics. I prefer dedicated forums like this one. You might also try eng-tips, forums.mikeholt, or ones sponsored by software vendors.
| Top |
NeDCE
Post subject: Re: Arc Flash Results Posted: Fri Mar 28, 2025 3:45 pm |
bbaumer wrote: Also, is that EasyPower? Should your most downstream feeders be 3-1/C, not 1-1/C? Not an EasyPower user so not sure. Attachment: conductors.jpg @bbaumer and also @jsoar: in EasyPower, "3-1/C" means three parallel conductors per phase in a single conductor cable configuration. So the first digit is how many (parallel) line conductors per phase, and the "X/C" is how many conductors in a cable configuration. So if I had a conductor run "1-3/C", that would be something in a 3-conductor cable assembly, such SO cable or something run in cable tray. A 3-phase circuit run showing "1-1/C" would be a standard 3-phase, one conductor-per-phase circuit. (note that neutral and ground are a separate tab and aren't addressed in that nomenclature)
| Top |
bbaumer
Post subject: Re: Arc Flash Results Posted: Sat Mar 29, 2025 2:04 am |
| Arc Level |
Makes sense. Thanks!