Author:  arcflashprimero [ Mon Jan 26, 2026 11:24 am ]
Post subject:  Relay modeling

Do you model anything other than 50/51 settings for relays?

Author:  bbaumer [ Tue Jan 27, 2026 4:24 am ]
Post subject:  Re: Relay modeling

The CT ratio, curve type, any time delays or definite time setting and the breaker clearing time.

Author:  arcflashprimero [ Tue Jan 27, 2026 6:13 am ]
Post subject:  Re: Relay modeling

Thanks! What about upstream transformer differential protection and generator protection. Will these affect the arc flash calculations?

Author:  bbaumer [ Tue Jan 27, 2026 7:12 am ]
Post subject:  Re: Relay modeling

Just depends on what the settings are and what breaker or breakers they are controlling and what other protection downstream busses have or don't have. I do model them and include the settings for record if nothing else but it is possible that they will affect IE, again, just depends on the setup.