In Performing a study for example, with a secondary service at 480 volts and a 2500 KVA utility owned transformer, if you include the utility fuse on the primary of the transformer it could reduce the line side energy at the customer incoming PD.
On the other hand, you have no control of the utility fuse which can change at any time without notice to the customer, so this would mean do not include the utility fuse.
Thoughts, comments... thanks Jimmy


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Philosophy
PostPosted: Thu Apr 30, 2026 9:39 am 
Arc Level

Joined: Tue Jan 13, 2009 5:00 pm
Posts: 631
In my experience, utilities have consistent primary fusing based on transformer KVA. A simple fuse replacement will be of the same size.
On the other hand, should a transformer require replacement, you might not get the same impedance or KVA. Best to check back periodically.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Study Philosophy
PostPosted: Sun May 03, 2026 1:28 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
I either don't model the fuse or I make it fail to operate as I have found it is difficult to get the primary side fuses to blow on a arcing fault "in real life" and it cannot be counted on to clear secondary faults quickly.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883