Anyone figure out how to simulate this in EasyPower or how to calculate the hazards for this type of system?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Oct 09, 2009 12:41 pm 
Offline
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
I have talked to ESA about this. As of now there is no AF calculations for single phase voltages that they utilize.

You have a couple of choices.
Click on the bus properties open the Arc FLash tab, 1. You can exclude the calculation until proper data creates a software upgrade to include single phase faults. 2. You can reference the upstream protective device and put in a simulated fault clearing time say 0.3sec. 3. You can enter the cal's/cm2 as a value you have calculated or your plans say to use for such cases as a default.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Oct 19, 2009 1:34 pm 
Offline
Sparks Level
User avatar

Joined: Sun Aug 16, 2009 8:42 am
Posts: 184
Location: Lawrenceburg KY
I seen were Zog posted this comment about SKM and single phase modeling.

Zog says, "You need to purchase the single phase module from SKM."


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 29, 2009 1:02 pm 
Offline

Joined: Thu Jun 11, 2009 12:38 pm
Posts: 33
Location: Kansas city
SKM does not calculate arc flash incident energy for the single phase system either. The single phase module they have is good for load flow studies and short circuit studies.
A conservative approach to modeling the single phase system is to model it as a 3-phase system. Your software can then use the 1584 equations to provide you the desired results.

There are couple of threads in this forum which discuss more on this subject.

Regards.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Oct 29, 2009 1:05 pm 
Offline
Sparks Level

Joined: Thu Jul 19, 2007 7:54 am
Posts: 201
Location: St. Louis, MO
I haven't seen it, but the latest advertisement from ETAP is that they perform single phase arc flash studies.
I would like to know what there calculation is based on.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883