 Post subject: What's wrong here
PostPosted: Thu Sep 22, 2022 6:19 am 
Sparks Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 373
Location: Indiana
Came across these in the same facility a couple days ago.

The first one is easy.

Who can say what is wrong with the second?

Attachment:
disconnect1.jpg
disconnect1.jpg [ 140.62 KiB | Viewed 13324 times ]


Attachment:
fused disconnect1.jpg
fused disconnect1.jpg [ 130.84 KiB | Viewed 13324 times ]


Attachment:
fused disconnect close.jpg
fused disconnect close.jpg [ 235.98 KiB | Viewed 13324 times ]


Attachments:
image001 (1).png
image001 (1).png [ 974.24 KiB | Viewed 13324 times ]

_________________
SKM jockey for hire
PE in 16 states
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What's wrong here
PostPosted: Thu Oct 27, 2022 7:10 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 881
Location: Rutland, VT
First one is easy as it is wire used in place of a fuse.

Second one took some looking but it looks like the mounting stud was broken on the left most pole and a new hole drilled to accomodate a new bolt for the lug. That is my guess.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What's wrong here
PostPosted: Tue Dec 06, 2022 11:53 am 
User avatar

Joined: Wed Nov 23, 2022 8:53 am
Posts: 15
Location: Indiana
Yeah, first one is using wires in place of fuses, but I can't find where that is a code violation. The issue I see is they are vastly undersized compared to the rest of the circuit. They are also using SIMpull Alumaflex wire, might want to make sure the terminals allow that.

For Pic #2, it is common convention to use Brown, Orange and Yellow for 480Y/227 Vac wiring, but it is not a Code requirement [but it is for Purdue ;) ]. Therefore, I'm guessing you have 250V fuses on a 480V system. Yikes! A second possible issue, it looks like all the wire is going in and out of the same conduit, and is possibly #1/0, possibly Alumaflex again. If these things are true, your wire is again vastly undersized.

_________________
Steward of the magic smoke genie.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: What's wrong here
PostPosted: Thu Dec 22, 2022 9:53 am 
Sparks Level

Joined: Tue Jan 19, 2010 2:35 pm
Posts: 174
Here's something that happened to me years ago. I opened a 30 amp 3 pole fused disconnect to see if all the blades were pulled away from the line side. All were. Then I checked for voltage. A phase was still energized even though the blades were clearly disconnected. Taking a closer look, I found a wire jumper from the line to load side AROUND the A phase 30 amp fuse. I guess the fuse was blown and someone could not be bothered to get a new fuse.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883