phil.haataja
|
Post subject: Voltage rated gloves Posted: Mon May 09, 2022 3:04 pm |
|
Joined: Fri Sep 24, 2021 7:17 am Posts: 18
|
So......NFPA 70E states the limited approach boundary for 120VAC is "avoid contact"
Does that mean I can use a multimeter without voltage-rated gloves if I don't touch the energized 120VAC device with my body.....or is my meter "contacting" it.....thus requiring shock protection gear?
|
|
Top |
|
 |
mpparent
|
Post subject: Re: Voltage rated gloves Posted: Tue May 10, 2022 6:26 am |
|
Joined: Thu Apr 18, 2019 11:42 am Posts: 77
|
My opinion is that voltage rated gloves are not required for this work, since you'll have rated voltage probes as your means to "avoid contact".
Mike
|
|
Top |
|
 |
|