Canuck01 wrote:
Sorry, maybe I wasn't clear...
Do you consider the act of throwing a disconnect to apply a lockout for non-electrical work a hazard which requires Arc Flash protective gear? If so, why?
Sorry I wasn't clear. Yes, I do consider this an act that requires AF gear. Largely because you have now calculated the energy potential, and you KNOW that there is a risk and what the protection should be against the Arc Flash.
elihuiv wrote:
They are an estimate based on the committee's experience along with their "risk" factor. This wasn't scientific.
Exactly as Hugh says. The tables take into the account the 70E Committees SUBJECTIVE analysis of what the risk of an event happening may be, and what the damage could be. You have performed the analysis. You don't have the luxury of saying it Probably Won't Happen to This Guy.
Besides, would you rather he get burned AND broken bones?
jghrist wrote:
True, a high level arc may have an explosive force that blows the door off, but will wearing a Nomex shirt rated for 10 cal/cm² provide any protection against flying doors?