scottnimon@powersourceeng wrote:
PPE pertains primarily to energized work. If your qualified worker is exposed to energized parts within the Arc Flash Boundary, as determined from an arc flash study, he needs to be suited up in a PPE level equal to or greater than the incident energy level of the equipment.
The live parts do not need to be exposed for arc flash PPE to be required.
scottnimon@powersourceeng wrote:
Using NFPA table 130.7(C)(9), operating (resetting) a circuit breaker with the covers on requires PPE level 0. Voltage testing requires 2*.
I would not recommend using the tables for the OP here, with 4000A switchgear I highly doubt they are able to use the tables.