I have read on the forum that all clothing under PPE must be non-melting (i.e. not poly bend). I have a 2009 NFPA 70E handbook that seems to contradict this. In the interpretation section of 130.7(c)(5) Body Protection, is says
“Employees who are within the Arc Flash Protection Boundary must wear FR clothing for protection from the thermal effects of an arcing fault. The requirement is that all ignitable clothing must be protected by at least one layer of clothing that has an established incident-energy rating. Clothing could be shirt and pant, coveralls or any other assembly that provides protection for ignitable clothing or exposed skin.�
Could anyone help clear this up for me?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 13, 2010 11:52 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
130.7(C)(14) is pretty clear. I think you are confusing ignitable and melting. 100% cotton is ignitable, polyester is melting.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu May 13, 2010 12:22 pm 

Joined: Wed May 12, 2010 1:43 pm
Posts: 4
You are correct, I was confusing the two and yes 130.7(C)(14) is clear. Thank you for the clarification.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883