Arc Flash Forum
Repair Kit
https://brainfiller.com/arcflashforum/viewtopic.php?f=5&t=1293
Page 1 of 1
Author:  Allison White [ Mon Sep 20, 2010 8:11 am ]
Post subject:  Repair Kit
Has anyone recieved or heard of an FR repair kit? One that might include patches that you can heat seal?
Author:  Zog [ Mon Sep 20, 2010 9:11 am ]
Most PPE providers will give you a repair kit, keep in mind the manufacture will have specific repair guidelines and all materials used have to be FR, thread and patch (same ATPV rating for the patch).
Author:  Allison White [ Tue Sep 21, 2010 11:17 am ]
Thank you Zog
Author:  msaner@workrite.com [ Tue Sep 28, 2010 1:48 pm ]
Workrite has patch material that is of the heat transfer type. Below are the basic requirements.
General:
• The patching fabric must be the same as the garment fabric.
• For minor tears and thin spots apply per application instructions below.
• For holes; no adhesive is to be exposed to the skin
• Patches should not exceed 2” x 4”.
Application:
• Use a heat press
• Upper plate temperature 400° F
• Lower plate temperature 350° F
• Press load 80 lbs.
• Dwell time 10 seconds