 Post subject: Hazard/Risk Category #1 PPE
PostPosted: Tue Jun 17, 2008 8:12 am 

Joined: Tue Mar 25, 2008 1:00 pm
Posts: 32
Is the cal/cm^2 supposed to be 4 or 5 for hazard level 1? I see it listed in many places online as 5 cal/cm^2 and they claim its form the NFPA 70E, but the edition I have (2004) listed 4 cal/cm^2. Is this just a change between editions?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jun 17, 2008 8:32 am 
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
deprico wrote:
Is the cal/cm^2 supposed to be 4 or 5 for hazard level 1? I see it listed in many places online as 5 cal/cm^2 and they claim its form the NFPA 70E, but the edition I have (2004) listed 4 cal/cm^2. Is this just a change between editions?


Yep, was 5cal/cm2 in 2000 and changed to 4 cal/cm2 in 2004 edition.