Arc Flash Forum https://brainfiller.com/arcflashforum/ |
|
Hazard/Risk Category #1 PPE https://brainfiller.com/arcflashforum/viewtopic.php?f=5&t=145 |
Page 1 of 1 |
Author: | deprico [ Tue Jun 17, 2008 8:12 am ] |
Post subject: | Hazard/Risk Category #1 PPE |
Is the cal/cm^2 supposed to be 4 or 5 for hazard level 1? I see it listed in many places online as 5 cal/cm^2 and they claim its form the NFPA 70E, but the edition I have (2004) listed 4 cal/cm^2. Is this just a change between editions? |
Author: | Zog [ Tue Jun 17, 2008 8:32 am ] |
Post subject: | |
deprico wrote: Is the cal/cm^2 supposed to be 4 or 5 for hazard level 1? I see it listed in many places online as 5 cal/cm^2 and they claim its form the NFPA 70E, but the edition I have (2004) listed 4 cal/cm^2. Is this just a change between editions?
Yep, was 5cal/cm2 in 2000 and changed to 4 cal/cm2 in 2004 edition. |
Page 1 of 1 | All times are UTC - 7 hours |
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group http://www.phpbb.com/ |