Hi,
I'm writing an arc flash standard for my company and I am wrestling with the CAT 1 requirement for wearing leather gloves. Because our control voltages for controlling turbines and generators are typically 120 V (AC or DC), all employees working on the equipment would be required to wear leather gloves to perform any troubleshooting work which must be done live. From personal experience this is very difficult due to the small size of the equipment that's being worked on. There could be a risk to the equipment due to the lack of dexterity provided by the gloves. Does anyone have experience or advice on this issue?

Thanks,

W. Casey Harman


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Mon Feb 14, 2011 1:29 pm 
Offline
Plasma Level

Joined: Mon Jun 02, 2008 11:58 am
Posts: 1103
Location: Charlotte, NC
Well you need to wear rubber gloves for shock protection, but OSHA 1910.137 says this

(b)(2)(vii) Protector gloves shall be worn over insulating gloves, except as follows:

(b)(2)(vii)(A) Protector gloves need not be used with Class 0 gloves, under limited-use
conditions, where small equipment and parts manipulation necessitate unusually
high finger dexterity.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Feb 16, 2011 11:57 am 
Offline

Joined: Fri Jul 23, 2010 11:36 am
Posts: 15
Are you actually handling energized conductors, or is there some sort of insulation over the conductor?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Feb 16, 2011 10:05 pm 
Offline
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
One thing I have found with the whole "Arc Flash" issue is now wearing Class 0 Rubber gloves with Leather Protectors... Personally I find them too warm, and I notice my hands are sweating alot more than before with just leather gloves.. Not to mention the reduced dexterity.. It is almost getting to be more of a hazzard that just leathers or even (heaven forbid) barehands..

Before the flood gates open, I am not dumb enough to use bare hands in close proximity to a live bus... But connecting wires to de-energized breakers in a panel the gloves have caused me to have to "relearn" my sense of touch with the gloves on...


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Wed Feb 16, 2011 10:07 pm 
Offline
Sparks Level

Joined: Mon Mar 29, 2010 5:02 am
Posts: 136
hurricane harry wrote:
Are you actually handling energized conductors, or is there some sort of insulation over the conductor?


?? Are you asking about bare wires or insulated conductors (RW90, TEW, THHN, etc)?


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Feb 17, 2011 8:50 am 
Offline

Joined: Fri Jul 23, 2010 11:36 am
Posts: 15
glen1971 wrote:
?? Are you asking about bare wires or insulated conductors (RW90, TEW, THHN, etc)?


Yes, that's what I meant. If they are handling bare energized conductors, I would think that class zero's are manditory. If they are insulated, then the leathers only sounds like a company policy.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 6 posts ] 

All times are UTC - 7 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883